And in very northern climates, things don't dry out. So best to keep the moisture on the warm side of an interior vapor retarder as much as possible.
Original Message:
Sent: 03-26-2024 01:13 PM
From: Gregory La Vardera
Subject: Code Wall Assemblies - Alternate to Code described R20+R5continuous insulation.
Paul,
Exterior insulation can certainly warm the inside surface of the sheathing, and this can prevent condensation – if you are going to let interior conditioned air un-fettered access to your stud cavity. However, if you are controlling vapor at the inside of your wall assembly then in theory it should not be reaching the sheathing in any great volume to cause condensation. The caveat here is that kraft faced insulation is far from continuous, and electrical device boxes make regular holes in it.
When you use an exterior insulation that is not vapor open - such as a foam insulation layer - then you are adding a vapor retarder to the exterior (on top of your sheathing which is already a vapor retarder). So when you are going to do this, best practice is not to also put a vapor retarder at the interior - because it should be easy for the wall to dry-out in at least one direction.
When you use an exterior insulation that is vapor open - like mineral wool - this concern goes away, and you can control vapor at the interior side, which is more ideal and more resilient for heating climates in the Zones in question here.
Why is that? Because controlling vapor's entry into the stud cavity is always more effective placed at the interior side. If the wall experiences "out of range" conditions it will still perform perfectly. By "out of range" conditions I mean like when an Arctic air mass sinks into the central US, and temperatures drop to the teens in Texas. While this is going on, Northern central States are experience -30F. Not just overnight either - we seen it recent winters for a week or more. Under these conditions the vapor closed exterior insulation wall may experience back of sheathing temperatures below the interior dew point for extended periods. Will it make your house fall down? No. Will it cause mold? Maybe. But in general, its clear that this is not a smart approach in many locations.
This whole discussion about the merits of where you control vapor in a wall assembly is way beyond the purpose of this White Paper, which is just to document that the interior continuous insulation wall is compliant with Code. The benefit is that these walls are easier and faster to build, and cost less in time and money.
------------------------------
Gregory La Vardera
Gregory La Vardera Architect
Merchantville NJ
------------------------------
Original Message:
Sent: 03-26-2024 12:52 PM
From: Paul M. Reynolds AIA
Subject: Code Wall Assemblies - Alternate to Code described R20+R5continuous insulation.
My understanding is that's the entire point of the exterior insulation... not for insulation's sake but to keep the sheathing warm(er) and reduce the risk of condensation. Pushing the dew point...
I need to dig into the white paper, yet... It's also possible that I'm missing something.
------------------------------
Paul Reynolds AIA
HAUS | Architecture For Modern Lifestyles
Indianapolis IN
Original Message:
Sent: 03-25-2024 11:01 PM
From: Gregory La Vardera
Subject: Code Wall Assemblies - Alternate to Code described R20+R5continuous insulation.
Hi Jonathan, thanks for looking.
In short no hygrothermal analysis is included in the White Paper because the Code tables that relate insulation requirements does not address this.
That said the assemblies described in the Code, and the alternates we describe are not universal - no assembly is. People building in "micro" climate zones will always have to be mindful of the assemblies vapor performance. I will say that the assembles we describe with continuous insulation at the interior side are much more resilient than Code described walls with vapor retarding exterior insulation.
Greg
------------------------------
Gregory La Vardera
Gregory La Vardera Architect
Merchantville NJ
Original Message:
Sent: 03-25-2024 05:42 PM
From: Jonathan Huffmaster AIA
Subject: Code Wall Assemblies - Alternate to Code described R20+R5continuous insulation.
I see a WUFI model was created, but do not see a hygrothermal analysis. Could you please point us to that data or share, if not included in the white paper? The location of the vapor barrier may prove problematic in some (micro)climate zones.
------------------------------
Jonathan Huffmaster AIA
Architectural Design Group, pllc
Ham Lake MN